25% of the EPA 608 · blueprint 40 CFR part 82 subpart F, appendix D, section d (test content)

Short answer

Type III certifies work on low-pressure appliances — those using a refrigerant with a liquid-phase saturation pressure below 45 psia at 104 °F, such as R-11, R-123 and R-245fa. Low-pressure centrifugal chillers run under a vacuum, which inverts most of what Type II teaches: leaks draw air and moisture in rather than pushing refrigerant out, recovery is to 25 mm Hg absolute, and pressurising for a leak test is done with controlled heat first, with nitrogen only as the fallback.

Why it matters on this exam

Type III is the section where transferring Type II habits actively costs marks. A low-pressure machine operates below atmospheric pressure, so a leak lets air and moisture in. That single fact explains the purge unit, the freeze risk, the pressurisation rules and most of the 25 items.

Key concepts

Common mistakes

Worked example

An R-11 centrifugal chiller is purging far more often than it used to. On a machine running under a vacuum, that points to air and moisture being drawn in through a leak rather than refrigerant escaping — which is why the same symptom means something different here than on a high-pressure system. Before opening it for a non-major repair, note that R-11 boils at about 75 °F at atmospheric pressure, at or below the 85 °F line, so you must not use a method such as nitrogen that requires subsequent purging; you pressurise with controlled heat (hot water or a built-in heating device) to no higher than 0 psig. If you were recovering for service instead, the target is 25 mm Hg absolute, with the chiller water circulating throughout.

Original practice questions

Type III — low-pressure appliancesDifficulty 3/5

What evacuation level does Table 1 require for a low-pressure appliance?

  1. ATwenty-five inches of mercury vacuum, whatever the age of the recovery equipment
  2. BTen inches of mercury vacuum, if the recovery equipment was made after 1993
  3. CFifteen inches of mercury vacuum, if the charge is two hundred pounds or more
  4. DTwenty-five millimetres of mercury absolute, whatever the age of the equipment
Show answer and rationale

Correct: D. The low-pressure row is the only one in Table 1 expressed as an absolute pressure rather than a vacuum, and the only one that does not change with the age of the recovery equipment.

  • A — The figure is twenty-five millimetres of mercury absolute, not twenty-five inches of vacuum.
  • B — Ten inches applies to high-pressure appliances of two hundred pounds or more.
  • C — Fifteen inches applies to medium-pressure appliances of two hundred pounds or more.
Type III — low-pressure appliancesDifficulty 2/5

A low-pressure centrifugal chiller has begun purging far more frequently than before. What does this most likely indicate?

  1. AAir and moisture are being drawn into the system through a leak below atmospheric
  2. BRefrigerant is escaping from the system through a leak above atmospheric pressure
  3. CThe chiller is overcharged and the purge unit is removing the excess refrigerant
  4. DThe purge unit has failed and is cycling without removing any gas from the system
Show answer and rationale

Correct: A. A low-pressure machine runs below atmospheric pressure, so a leak lets air in rather than letting refrigerant out. The purge unit then works harder removing the non-condensables, which is the signature symptom.

  • B — The system sits below atmospheric pressure, so the pressure gradient drives air inward.
  • C — Purge units remove non-condensable gases, not surplus refrigerant from an overcharge.
  • D — A failed purge unit would show as rising non-condensables, not as increased purging.
Type III — low-pressure appliancesDifficulty 4/5

Why must water be circulated through or removed from a chiller while its refrigerant is being evacuated?

  1. AWater circulation is required to keep the purge unit operating during the evacuation
  2. BBoiling refrigerant absorbs heat and standing water in the tubes will freeze and split them
  3. CCirculating water raises the system pressure and shortens the time recovery takes
  4. DMoving water prevents sediment settling and blocking the evaporator tube bundle
Show answer and rationale

Correct: B. Evaporating refrigerant draws its latent heat from whatever is nearest, which is the water in the tubes. Ice expands, and a split tube bundle is an expensive and entirely avoidable failure.

  • C — Circulation does not meaningfully raise system pressure or accelerate the recovery.
  • D — Sediment is a maintenance concern generally, not the reason for circulating during evacuation.
  • A — Purge units operate independently of whether the chiller water is moving.
All 5 Type III — low-pressure appliances questions →

Tools for this topic

6 flashcards for Type III — low-pressure appliances

Practice this topic

Blueprint-mapped questions with full rationales for every choice.

Start practice
Related areas: Core · Type I — small appliances · Type II — medium, high and very high-pressure appliances

Primary references

  1. 40 CFR Part 82 Subpart F — Recycling and Emissions Reduction — Office of the Federal Register (eCFR) · government · retrieved 2026-09-22, verified 2026-09-22
  2. Section 608 Test Topics — United States Environmental Protection Agency · primary · retrieved 2026-09-22, verified 2026-09-22
Last reviewed: 2026-10-18Next review by: 2026-12-17Reviewed by: Openverse editorial team, Authoring and fact verificationHow we verify facts