Type II — medium, high and very high-pressure appliances

25% of the EPA 608 · blueprint 40 CFR part 82 subpart F, appendix D, section d (test content)

Short answer

Type II certifies work on medium-, high- and very high-pressure appliances other than small appliances, MVACs and MVAC-like appliances. Its 25 items are the densest on the exam: the Table 1 evacuation levels, which change with charge size and with whether the recovery machine predates 15 November 1993, the leak rate thresholds, major versus non-major repairs, and the prohibition on system-dependent equipment above 15 pounds.

Why it matters on this exam

Type II is where the numbers are, and where most candidates lose marks. Nearly every question reduces to identifying two things first — what pressure class the appliance is, and how big its charge is — before any rule can be applied.

Note the scope mismatch you will see elsewhere: EPA's website labels Type II "High-Pressure", but 82.161(a)(1)(ii) covers medium-, high- or very high-pressure appliances. The regulation is the authority.

Key concepts

| Appliance | Before 15 Nov 1993 | On or after | |---|---|---| | Very high-pressure | 0 | 0 | | High-pressure, charge under 200 lb | 0 | 0 | | High-pressure, charge 200 lb or more | 4 | 10 | | Medium-pressure, charge under 200 lb | 4 | 10 | | Medium-pressure, charge 200 lb or more | 4 | 15 | | Low-pressure | 25 mm Hg absolute | 25 mm Hg absolute |

Common mistakes

Worked example

A supermarket rack using R-22 holds 260 pounds and needs a compressor replaced; the shop's recovery machine is from 2018. R-22 is high-pressure, the charge is 200 pounds or more, and the machine is post-1993, so Table 1 requires 10 inches of mercury vacuum. If instead the job were a non-major repair with no later evacuation to atmosphere, 0 psig would do. And because the charge exceeds 50 pounds and this is commercial refrigeration, a leak rate above 20 percent would start a 30-day repair clock for the owner.

Original practice questions

Type II — medium, high and very high-pressure appliancesDifficulty 4/5

A high-pressure appliance holds a full charge of 260 pounds and the recovery machine was made in 2018. What evacuation level does Table 1 require?

  1. AFifteen inches of mercury vacuum, because the recovery machine postdates the rule
  2. BZero inches of mercury vacuum, because high-pressure appliances have no requirement
  3. CTen inches of mercury vacuum, because the charge is two hundred pounds or more
  4. DFour inches of mercury vacuum, because the appliance operates at high pressure
Show answer and rationale

Correct: C. Table 1 splits high-pressure appliances at two hundred pounds. Under that figure the requirement is zero; at or above it the requirement is four inches for pre-1993 equipment and ten inches for later equipment.

  • D — Four inches is the pre-15 November 1993 equipment figure; this machine was built in 2018.
  • A — Fifteen inches applies to medium-pressure appliances of two hundred pounds or more.
  • B — Zero applies only to high-pressure appliances with a charge under two hundred pounds.
Type II — medium, high and very high-pressure appliancesDifficulty 3/5

Under 40 CFR 82.157, what annual leak rate triggers the repair requirement for commercial refrigeration equipment?

  1. AThirty percent, for appliances with a full charge of fifty pounds or more
  2. BTen percent, for appliances with a full charge of fifty pounds or more
  3. CFifteen percent, for appliances with a full charge of twenty pounds or more
  4. DTwenty percent, for appliances with a full charge of fifty pounds or more
Show answer and rationale

Correct: D. Section 82.157(c)(2) sets three thresholds: twenty percent for commercial refrigeration, thirty percent for industrial process refrigeration, and ten percent for comfort cooling and everything else. All are gated on a fifty-pound full charge.

  • A — Thirty percent is the industrial process refrigeration threshold, not the commercial one.
  • B — Ten percent covers comfort cooling and other appliances not in the first two categories.
  • C — Fifteen percent is not a threshold in the rule, and the charge gate is fifty pounds.
Type II — medium, high and very high-pressure appliancesDifficulty 3/5

After reaching the required recovery vacuum, the system pressure rises again over the next few minutes. What does this indicate?

  1. ALiquid refrigerant remains in the system or is dissolved in the compressor oil
  2. BThe recovery machine has failed and its internal valves are leaking backwards
  3. CThe required level was exceeded and refrigerant is being drawn back into the system
  4. DNon-condensable gases have entered and must be purged before work can continue
Show answer and rationale

Correct: A. Refrigerant dissolved in oil boils off slowly, raising the pressure after the gauge first reaches target. This is why the topic list tells you to wait and watch rather than disconnect immediately.

  • B — A machine fault would show as a failure to reach the level, not as a slow rise after it.
  • C — Recovery machines do not push refrigerant back into an appliance once the level is reached.
  • D — Non-condensables are a low-pressure system concern and would not appear at this point.
All 5 Type II — medium, high and very high-pressure appliances questions →

Tools for this topic

6 flashcards for Type II — medium, high and very high-pressure appliances

Practice this topic

Blueprint-mapped questions with full rationales for every choice.

Start practice
Related areas: Core · Type I — small appliances · Type III — low-pressure appliances

Primary references

  1. 40 CFR Part 82 Subpart F — Recycling and Emissions Reduction — Office of the Federal Register (eCFR) · government · retrieved 2026-09-22, verified 2026-09-22
  2. Section 608 Test Topics — United States Environmental Protection Agency · primary · retrieved 2026-09-22, verified 2026-09-22
Last reviewed: 2026-10-18Next review by: 2026-12-17Reviewed by: Openverse editorial team, Authoring and fact verificationHow we verify facts