25% of the EPA 608 · blueprint 40 CFR part 82 subpart F, appendix D, section d (test content)

Short answer

Type I certifies you to maintain, service or repair small appliances — units manufactured, charged and hermetically sealed in a factory with five pounds of refrigerant or less. Its 25 items concentrate on recovery: the 80 and 90 percent thresholds, the four inches of mercury alternative, passive recovery from a unit whose compressor has failed, and access valves. It is the only type that may be offered as a mail-in test.

Why it matters on this exam

Type I is the narrowest section and the most formulaic, which makes it the cheapest 25 items on the test if you learn the recovery numbers exactly. It is also the section most often oversimplified, because the three recovery options are routinely collapsed into one.

Key concepts

  1. recover 80 percent of the refrigerant, if the equipment was manufactured before 15 November 1993; or
  2. with equipment manufactured on or after that date, recover 90 percent when the appliance's compressor is working, or 80 percent when it is not; or
  3. evacuate the appliance to four inches of mercury vacuum.

Common mistakes

Worked example

A domestic refrigerator with a seized compressor is going to the tip. You have a recovery machine built in 2015. The 90 percent figure does not apply, because the compressor is not functioning — you need 80 percent, or you can evacuate to four inches of mercury instead. Using a system-dependent device you would install access valves on both the high and low sides, since the appliance cannot move its own refrigerant. And the person actually disposing of the unit does not need to hold any certification, though the recovery rule still applies to the work.

Original practice questions

Type I — small appliancesDifficulty 2/5

Under 40 CFR 82.152, which description matches the definition of a small appliance?

  1. AFully manufactured and charged on site with twenty pounds or less of any refrigerant
  2. BFully manufactured, charged and hermetically sealed in a factory with five pounds or less
  3. CAny self-contained unit holding five pounds or less, whether factory sealed or field charged
  4. DAny domestic refrigeration unit sold for household use regardless of its refrigerant charge
Show answer and rationale

Correct: B. All three conditions in the definition matter together: factory manufactured, factory charged, and hermetically sealed, with a charge of five pounds or less. A field-charged unit is not a small appliance however small it is.

  • C — Factory sealing is part of the definition; a field-charged unit falls outside it entirely.
  • D — The definition is about construction and charge size, not about who the unit was sold to.
  • A — Twenty pounds is the MVAC-like threshold, and on-site charging excludes a unit from the definition.
Type I — small appliancesDifficulty 3/5

Using recovery equipment manufactured in 2015 on a small appliance whose compressor no longer runs, what must you achieve?

  1. ARecover ninety percent of the charge, or evacuate to ten inches of mercury vacuum
  2. BRecover one hundred percent of the charge before the appliance may be opened at all
  3. CRecover eighty percent of the charge, or evacuate to four inches of mercury vacuum
  4. DRecover ninety percent of the charge, or evacuate to four inches of mercury vacuum
Show answer and rationale

Correct: C. Section 82.156(b)(2) makes the ninety percent figure conditional on the compressor functioning. With a dead compressor and post-1993 equipment the requirement drops to eighty percent, and the four inches of mercury option under 82.156(b)(3) remains available either way.

  • D — Ninety percent applies only when the appliance's compressor is working; this one is not.
  • A — Ten inches of mercury is a Table 1 figure for larger appliances, not a small-appliance option.
  • B — The rule never requires complete recovery; it sets percentage and vacuum thresholds instead.
Type I — small appliancesDifficulty 3/5

Why must both high and low side access valves be installed when recovering from a small appliance with an inoperative compressor?

  1. AThe recovery machine requires two connections before its internal pump will start up
  2. BRegulations require two access points on every small appliance being serviced or opened
  3. CThe second valve provides a route for nitrogen to be introduced during the recovery
  4. DNothing in the appliance can move refrigerant from one side of the system to the other
Show answer and rationale

Correct: D. A system-dependent device relies on the appliance's own compressor to shift refrigerant. With the compressor dead, refrigerant trapped on the far side of the restriction has no path out unless you open both sides.

  • A — Recovery machines do not impose a two-connection requirement of their own to operate.
  • B — The rule does not require two access points generally; the reason here is the failed compressor.
  • C — Nitrogen is a leak-detection gas and plays no part in recovering from a small appliance.
All 5 Type I — small appliances questions →

Tools for this topic

5 flashcards for Type I — small appliances

Practice this topic

Blueprint-mapped questions with full rationales for every choice.

Start practice
Related areas: Core · Type II — medium, high and very high-pressure appliances · Type III — low-pressure appliances

Primary references

  1. 40 CFR Part 82 Subpart F — Recycling and Emissions Reduction — Office of the Federal Register (eCFR) · government · retrieved 2026-09-22, verified 2026-09-22