Type III — low-pressure appliances: practice questions

5 original questions · 5 editor-approved · every choice explained.

Practice this topic

Blueprint-mapped questions with full rationales for every choice.

Start practice
Type III — low-pressure appliancesDifficulty 3/5

What evacuation level does Table 1 require for a low-pressure appliance?

  1. ATwenty-five inches of mercury vacuum, whatever the age of the recovery equipment
  2. BTen inches of mercury vacuum, if the recovery equipment was made after 1993
  3. CFifteen inches of mercury vacuum, if the charge is two hundred pounds or more
  4. DTwenty-five millimetres of mercury absolute, whatever the age of the equipment
Show answer and rationale

Correct: D. The low-pressure row is the only one in Table 1 expressed as an absolute pressure rather than a vacuum, and the only one that does not change with the age of the recovery equipment.

  • A — The figure is twenty-five millimetres of mercury absolute, not twenty-five inches of vacuum.
  • B — Ten inches applies to high-pressure appliances of two hundred pounds or more.
  • C — Fifteen inches applies to medium-pressure appliances of two hundred pounds or more.
Type III — low-pressure appliancesDifficulty 2/5

A low-pressure centrifugal chiller has begun purging far more frequently than before. What does this most likely indicate?

  1. AAir and moisture are being drawn into the system through a leak below atmospheric
  2. BRefrigerant is escaping from the system through a leak above atmospheric pressure
  3. CThe chiller is overcharged and the purge unit is removing the excess refrigerant
  4. DThe purge unit has failed and is cycling without removing any gas from the system
Show answer and rationale

Correct: A. A low-pressure machine runs below atmospheric pressure, so a leak lets air in rather than letting refrigerant out. The purge unit then works harder removing the non-condensables, which is the signature symptom.

  • B — The system sits below atmospheric pressure, so the pressure gradient drives air inward.
  • C — Purge units remove non-condensable gases, not surplus refrigerant from an overcharge.
  • D — A failed purge unit would show as rising non-condensables, not as increased purging.
Type III — low-pressure appliancesDifficulty 4/5

Why must water be circulated through or removed from a chiller while its refrigerant is being evacuated?

  1. AWater circulation is required to keep the purge unit operating during the evacuation
  2. BBoiling refrigerant absorbs heat and standing water in the tubes will freeze and split them
  3. CCirculating water raises the system pressure and shortens the time recovery takes
  4. DMoving water prevents sediment settling and blocking the evaporator tube bundle
Show answer and rationale

Correct: B. Evaporating refrigerant draws its latent heat from whatever is nearest, which is the water in the tubes. Ice expands, and a split tube bundle is an expensive and entirely avoidable failure.

  • C — Circulation does not meaningfully raise system pressure or accelerate the recovery.
  • D — Sediment is a maintenance concern generally, not the reason for circulating during evacuation.
  • A — Purge units operate independently of whether the chiller water is moving.
Type III — low-pressure appliancesDifficulty 4/5

What is the preferred method of pressurising a low-pressure system for a leak test?

  1. ACompressed air through a filter-drier, with nitrogen used only for large chillers
  2. BOxygen through a pressure regulator, with a relief valve fitted to the test line
  3. CControlled hot water or a built-in heating device, with nitrogen as the fallback
  4. DNitrogen through a pressure regulator, with controlled hot water as the fallback
Show answer and rationale

Correct: C. Heat is preferred because it needs no purging afterwards. Section 82.156(a)(1)(ii) makes the same distinction for non-major repairs, barring methods requiring subsequent purging where the refrigerant boils at or below 85 degrees Fahrenheit.

  • D — The order is reversed; nitrogen is the fallback precisely because it must be purged.
  • A — Compressed air introduces moisture and is not an approved leak-test pressurisation method.
  • B — Oxygen must never be used to pressurise a system containing refrigerant oil.
Type III — low-pressure appliancesDifficulty 3/5

When recharging a low-pressure centrifugal chiller, why is vapour introduced before liquid?

  1. ATo purge the non-condensable gases that collected while the system was open
  2. BTo confirm that the charging valve is clear before liquid refrigerant is added
  3. CTo allow the oil to warm to the temperature required before it can be removed
  4. DTo raise the temperature in the tubes so the water inside them does not freeze
Show answer and rationale

Correct: D. Liquid refrigerant entering an evacuated chiller flashes to vapour and chills the tubes sharply. Bringing the pressure and temperature up with vapour first removes that freezing risk, and charging goes through the evaporator charging valve.

  • A — Non-condensables are removed by the purge unit, not by the order in which you charge.
  • B — Valve clearance is confirmed before charging begins and is not the reason for the sequence.
  • C — Heating oil to 130 degrees Fahrenheit concerns oil removal, which precedes recharging.

Primary references

  1. 40 CFR Part 82 Subpart F — Recycling and Emissions Reduction — Office of the Federal Register (eCFR) · government · retrieved 2026-09-22, verified 2026-09-22
  2. Section 608 Test Topics — United States Environmental Protection Agency · primary · retrieved 2026-09-22, verified 2026-09-22